Hello Gentlemen, there has been some discussion about proper sizing of the motor starter, overloads, conductors, fuses and raceway. Being that Shane and Jude are headlining the wiring and we do not want to endanger our building compliance with such a large load. I took the time to figure this out for the pickle.

I used the motor nameplate, http://i.imgur.com/NRd46.jpg
And entered it into the motor branch circuit calculator based on the current 2011 NEC http://www.electrician2.com/calculators/motor_ver_1.html
The end result is this, http://i.imgur.com/gvuFu.png

I do not have Shane's contact information so if anyone reads this and sees him please direct him here.

Thank you.

_________________
Image


Top
 Profile  
 
 Post subject: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Tue Mar 20, 2012 7:18 pm 
Offline
User avatar

Joined: Wed Feb 29, 2012 8:53 am
Posts: 40
Location: Saint Paul
Also I took a good long look at Shane's very creative starting circuit. The man just looked at the old starter and thought for a minute and wired it up. I've not seen a latching circuit like this before mainly because I deal with new products in my line of work with the budget for a separate starting circuit with transformer to isolate it.

Please digest this, list any pros or cons you see in the design.

Image

_________________
Image


Top
 Profile  
 
 Post subject: Re: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Wed Mar 21, 2012 8:30 am 
Offline

Joined: Sat Jul 17, 2010 5:13 pm
Posts: 246
Location: Minneapolis, MN
Except for the addition of the control pushbuttons, that actually looks a lot like how the original starter was wired.

Sent from my Slider SL101 using Tapatalk

_________________
If it ain't broke, your version is outdated.


Top
 Profile  
 
 Post subject: Re: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Wed Mar 21, 2012 11:24 am 
Offline
User avatar

Joined: Thu Dec 02, 2010 12:25 pm
Posts: 75
Location: Minneapolis
Latching is kind of irrelevant. It goes when the pressure switch tells it to go, and stops when the pressure switch signals that the required pressure has been attained. The only thing you can really screw up when wiring a compressor is the heaters. You have to check the chart to make sure they are right for the voltage and HP.

-Jim Hart


Top
 Profile  
 
 Post subject: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Thu Mar 22, 2012 3:38 am 
Offline
User avatar

Joined: Wed Feb 29, 2012 8:53 am
Posts: 40
Location: Saint Paul
Jim, you are right.

_________________
Image


Top
 Profile  
 
 Post subject: Re: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Thu Mar 22, 2012 11:32 pm 
Offline
User avatar

Joined: Fri Feb 05, 2010 10:35 pm
Posts: 71
For the normal operation of home compressors you are correct. This however is designed to keep running. When it reaches a predetermed (sp) psi the valves on the top of the compressor will open up. The motor will not shut off. It utilizes unloading valves so that there isn't a constant starting and stopping of the 3 phase motor. That being said. We are wiring a switch to turn the compressor on so we don't run it when we don't need to. The decision (not mine) to utilize the push button was so that we had an emergency shut off. You can use a push button as a toggle switch if you "logic latch" it. I haven't had time to look at the current design as I've have been busy with school and other projects. (as always) If you need to look up the design of the compressor it is a curtis d97.

_________________
"insert something witty here"


Top
 Profile  
 
 Post subject: Re: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Fri Mar 23, 2012 12:42 pm 
Offline
User avatar

Joined: Thu Dec 02, 2010 12:25 pm
Posts: 75
Location: Minneapolis
Generally there is a manual valve to select between continuous and intermittent, If Curtis doesn't have one it would be a worthwhile addition. It's just a valve which turns the unloader on and off. The unloader is set for a lower pressure than the pressure switch, so when you close the valve and disconnect the unloader the compressor pumps up to the pressure switch setpoint and shuts off.

The rule of thumb is that if the compressor is in intermittent mode and you notice it turning on and running over 50% of the time, it's time to turn on the unloader and go to continuous mode, to save wear and tear on the motor and starter.

-Jim Hart


Top
 Profile  
 
 Post subject: Re: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Sat Mar 24, 2012 11:25 pm 
Offline
User avatar

Joined: Fri Feb 05, 2010 10:35 pm
Posts: 71
Isn't that what I said??

_________________
"insert something witty here"


Top
 Profile  
 
 Post subject: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Sun Mar 25, 2012 11:39 am 
Offline
User avatar

Joined: Wed Feb 29, 2012 8:53 am
Posts: 40
Location: Saint Paul
I think the end all to these questions can be located here http://us.fscurtis.com/support/faq.htm

_________________
Image


Top
 Profile  
 
 Post subject: Re: Curtis Air Compressor (AKA The Big Pickle)
PostPosted: Mon Mar 26, 2012 9:28 am 
Offline
User avatar

Joined: Thu Dec 02, 2010 12:25 pm
Posts: 75
Location: Minneapolis
Adam, not exactly. What you described was operation with continuous unloader without pressure switch. What I described was dual control.

-Jim Hart


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 24 posts ]  Go to page Previous  1, 2, 3  Next

All times are UTC - 6 hours


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
Template made by DEVPPL Flash Games